want to use 220dryer outlet to power110

Discussion in 'Grow Room Design/Setup' started by loizier, Feb 6, 2011.

  1. #1 loizier, Feb 6, 2011
    Last edited by a moderator: Feb 6, 2011
    i want to use my 220 dryer outlet to power 110 equipment like AC, fans, but NO 1000w LIGHTS.

    iv been looking at 'step down transformers' from 220 to 110. im willing to wire it to a dryer plug:smoke:. i just dont know how OR which transformer to get...theres a million of'em on google shopping. has anyone done this? or something like this?

    is there anything else i could do?

    does anyone know of a 'light controller box' that has a dryer power cord? or anything else that runs off of a dryer outlet that i could use?

    thankyou VERY MUCH!:wave:

    ps: my recepticle is like this one.:smoke:
     

    Attached Files:

  2. anybody?
     
  3. You don't need a transformer, and you could build your own control box if you wanted to. The “L” shaped connection should be wired to the neutral and using one of the straight connectors will give you 120vac. And wiring the other straight connector (hot) and again using the “L” (neutral) will give you another circuit.

    The only thing is if your house is very old (built before the 70's) the wire going to the “L” may be a ground instead of a neutral.
     
  4. awwww that is acually perfect buy a small panal box change your breakers to 50 amp if the line can hold 30 if he have to and then you can use smaller 15 amp breaker to distribute
    power around the room

    if the line is 10 to 12 gage use 30 amp breaker if bigger use a 50 also you can just use three wire on the 220 line and wire it like a stander 15 amp socket with 15 amp 120 breaker simple fix
     
  5. this, sir, would require the room to be electricity-free. i just cant do it. this is the flower room. we dont stop once it has happened.:)
     
  6. aaaahh. i have heard of this. my house IS odler than the 70's but maybe not the dryer plug...?

    how do you tell the difference? meanwhile, :rolleyes:i will learn how to use my voltimeter :(.
    if i plugged 110AC into a grounded "L"?
     
  7. #7 bentripin, Feb 8, 2011
    Last edited by a moderator: Feb 8, 2011
    Do you have a neutral?

    If its a 3 wire + ground 220 you can pull one hot and neutral and have 110 (wire up a subpanel so you can use each phase)

    If its 2 wire (2 hot and ground, no neutral) its 220 only, you cant pull 110 off safely and this is how most dryer plugs are in older houses. you'll have to run a neutral if you want to do 110 minimum, I'd replace the entire line.

    Newer code wont allow you to do a 220 w/out a neutral.
     


  8. there is no replacing atm. it is in my flower room. ill eat my dirty shorts:devious: before i shut my flower room down for that.:D

    im looking for something that i can plug into the 220 dryer outlet to run 110 devices, like fans, heater, dehey, atc.

    im currently running off of 3 fuses/breakers in the house. one breaker i use, uses an extention cord. i would like to get rid of the extention cord 'cause its a hazard.

    i would love something that looks like this but dont want to spend 300 on something i have to cut into and possibly break.
     

    Attached Files:

  9. #9 loizier, Feb 8, 2011
    Last edited by a moderator: Feb 8, 2011
    FOUND IT!:cool:

    i think:rolleyes:

    one MUST plug that 110 cord in for the unit to work. im sure theres a way to bypass this.

    uses a 4 pin dryer cord...:(
     

    Attached Files:

  10. If the dryer outlet was added later it might work,
    Ben is correct, you need to find out if you have a neutral to the dryer outlet, turn off the breaker to the outlet and remove it from the wall to see how many wires are there, if it is a 4 wire you have most likely a black (hot), red (hot), white (neutral), green or bare copper (ground) (the copper may be connected to the box not the outlet) you only need to install a 4 prong outlet.

    If it is an older setup you will only have three wires a black and red or 2 blacks and a bare copper, if that is the case you would need to run a neutral (I too would replace the entire wire) to the outlet and swap the outlet to a 4 prong to be able to use it safely.

    You could wire a dryer cord to a couple of outlets and just plug it in, it would work but is less than safe. If you decide to do that at least try to run a ground to a cold water pipe. But I still would not recommend it.
     

    Attached Files:

  11. #11 loizier, Feb 8, 2011
    Last edited by a moderator: Feb 8, 2011
    im not trying to be a dick but IM NOT GOING TO REWIRE ANYTHING RIGHT NOW. this is in my flower room which will be occupied untill august. if i wanted to rewire stuff, i would have posted this in the diy section.:)

    right now i need something that is pretty much plug-and-play. which i think iv found :hello:.

    basically this is the diy step down transformer on the net...i think. and its sold on the cheapest place on the net;) 120V 4-Light Control w/Delay (240 input) | Grow Light Accessories

    :wave:

    FUCK 4 pin dryer cord....:mad::confused: now an adapter for the plug? this is getting expensive quick. but at least i know what im swimming in.:eek:
     

    Attached Files:

  12. #12 StinkBomb, Feb 8, 2011
    Last edited by a moderator: Feb 8, 2011

    PowerBox makes what you want. I use their products, and they are top of the line. I use multiple DPC-7500 units to power all my lights, movers, fans, etc... They make much bigger units, but I prefer fail safe redundancy in my grow rooms.

    Anyhow, they have many modles that plug into a standard dryer plugs, or can be wired for any plug type. They also have built in timers if you decide you want to run things on timed cycles.

    This is the one you want:

    [​IMG]

    [​IMG]

    Here is one with six 240 outlets on the left and six 120 outlets on the right.

    [​IMG]

    Here is a room running three combos (4x240, 2x120) and two with 120 outlets only.

    [​IMG]

    Looks like they retail for about $360. I don't know what I paid for mine.

    http://www.powerboxinc.com/7500_combo.html
     

  13. yea i was looking at that 30 amp timers box as well does anyone on here use one. thats the unit i was gonna post up for you... i dont know what that 120 cord is for though.
     
  14. #14 bentripin, Feb 9, 2011
    Last edited by a moderator: Feb 9, 2011
    You will never run any 110v equipment off that 220v 3 prong dryer plug, ever... nothing you plug in will be safe... give it up.

    You can pull 110v off a 220v line ONLY if it has a neutral (4 wire).. if it does not have a neutral it is 220 ONLY. This is why nobody makes this with the plug you need, its not safe.. dont swap plug ends unless you want to burn your house down.

    you can change the entire circuit to 110v since its a 3 wire, take one of the hots and make it a neutral and hook it up to a single pole 20A breaker... your colors wont be standard, but that dont mean anything if your carefull... if you want to keep it 30A you will need a 30A 110 outlet and a power distribution unit that takes the 30A 110 and splits it out into two 15A circuits with normal outlets.

    For example, remove the connecting bar that hooks the two breakers together on the double pole 30A in your fuse box.. pull one of the hot lines off this circuit and hook it to your grounding bar, this is now neutral. Then get a L5-30 Twistlock 30A receptacle to replace your dryer receptacle. Use a power distribution unit to make it available to a bunch of normal outlets.. http://www.nextdaypc.com/main/products/details.aspx?PID=A371150&rsmainid=ND0130014
     
  15. Yeah, the PowerBox stuff uses 4-wire 240 volt service to run the 120v outlets.
     
  16. i agree with ben, you should open that outlet or check at the panel for that neutral. it should be a 10/3 which is red black white with a #12 ground. even if u get the box itd be good to know, especially if you are using electronics on those ccts.
     
  17. If you have to just plug something in, keep using your extension cord until you can get in there and to this properly... yes its a hazard, but not as much as trying to get 110v off a 220v w/no neutral.... putting load on a ground is just plain stupid.
     

  18. yea, yea. this is what i was thinking all day yesterday when i found out that the straight pins have 120/110 EACH. for a total of +/-240. ground is dead. which means its not an Alternating Current if i only use ONE 110 pin and ONE pin thats basically stuck in the ground:confused:

    im going to re-read every post and google everything i didnt understand (which was a lot)...when im not waked-n-baked.
     